Post 1: Summary Recommendations
Post 2: Results
Post 3: Methods
Post 4: Conclusions
Posts 5 to 35: Details on the fans and their noise
What fans do you use with a Megahalems?
Well, with an i7 860 overclocked to 4GHz, you either use a single San Ace 9G1212H101/9G1212H1011, or you use a pair of Yate Loon D12SH-12's.
For details on how 65 fans fared in 112 setups, see below.
ehume is offline
post #2 of 411 (permalink) Old 05-02-2010, 03:55 PM - Thread Starter
Retired Reviewer
ehume's Avatar
The fans and their performance, arranged alphabetically
Fan List
This list has the fans in alphabetical order. The underlined bits link to the posts with the fan details.
Akasa Apache
Antec TriCool H
Antec TriCool L
Antec TriCool M
Arctic Cooling 12L
Bulk generic
Centaur x 2 @5v (Japan Servo)
CM BladeMaster (Cooler Master)
CM BladeMaster x 2 (Cooler Master)
CM R4 (Cooler Master)
Coolink SWiF2
Delta WFB1212H
Delta WFB1212H x 2
EBM 38mm (Papst)
Enermax Cluster
Enermax Magma
Evercool RSF-14
FDB-12-1300 (Sony/Thermalright)
FN-121 (Silverstone)
Gelid S12 (Gelid Solutions)
GT-1150 (Scythe/Nidec-Servo)
GT-1450 (Scythe/Nidec-Servo)
GT-1450 x 2 (Scythe/Nidec-Servo)
GT-1850 (Scythe/Nidec-Servo)
GT-1850 x 2 (Scythe/Nidec-Servo)
Kaze Maru 1200 (Scythe 140x25mm fans)
Kaze Maru 1900 (Scythe 140x25mm fans)
Kaze Maru 1900 x 2 (Scythe 140x25mm fans)
Kaze Maru 2 1700 (Scythe 140x25mm fans)
Magma+Cluster (Enermax)
MassCool FD12025
MassCool FD14025
MechaT 38mm @5v (MechaTronics)
MechaTronics 38mm
MechaTronics 120mm
Nexus Real Silent
NMB Panaflo Med
NMB [email protected]
Noctua NF-P12
Noctua NF-P12 x 2
Noctua NF-P14
Noctua NF-P14 x 2
Noctua NF-S12B
Noctua P12+S12B
NZXT
OKGear 2wire
OKGear 3wire
Papst 25mm
Papst 32mm
RFA-120BL (Rosewill)
RFX-120BL (Rosewill)
SA-9G1212E1011 (Sanyo Denki)
SA-9G1212G101 (Sanyo Denki)
SA-9G1212H101 (Sanyo Denki)
SA-9G1212H101 x 2 (Sanyo Denki)
[email protected] (Sanyo Denki)
SA-9G1212M101 (Sanyo Denki)
SA-9G1212P4G03 (Sanyo Denki)
SA-9G-E1011 @5v (Sanyo Denki)
SA-9G-G101 @5v (Sanyo Denki)
SA-9G-H101 [email protected] (Sanyo Denki)
SA-9G-P4G03 @5v (Sanyo Denki)
SA-9G-P4G03 x 2 (Sanyo Denki)
SA-9G-P4G03 [email protected] (Sanyo Denki)
SA-9S1212F401 (Sanyo Denki)
SA-9S1212H401 (Sanyo Denki)
SA-9S1212H401 x 2 (Sanyo Denki)
SA-9S1212L401 (Sanyo Denki)
SA-9S-H401 @5v (Sanyo Denki)
SA-9S-H401 x 2 @5v (Sanyo Denki)
Scythe generic
Servo Centaur (Japan Servo)
Servo Centaur @5v (Japan Servo)
Servo round (Japan Servo)
Servo round @5v (Japan Servo)
Servo round x2 (Japan Servo)
ServoCentaur x 2 (Japan Servo)
S-FLEX 1200 (Sony/Scythe)
S-FLEX 1600 (Sony/Scythe)
S-FLEX 1900 (Sony/Scythe)
SlipStream1200 (Scythe)
SlipStream1200 x 2 (Scythe)
SlipStream1600 (Scythe)
SlipStream1600x2 (Scythe)
SlipStream1900 #1 (Scythe)
SlipStream1900 #2 (Scythe)
SlipStream1900 x 2 (Scythe)
[email protected] (Scythe)
TT-A2018 (Thermaltake)
TT-A2018 @5v (Thermaltake)
TT-A2018 x 2 (Thermaltake)
TT-A2018 x 2 @5v (Thermaltake)
Ultra Kaze 1000 (Scythe Ultra Kaze)
Ultra Kaze 2000 (Scythe Ultra Kaze)
Ultra Kaze 2000 @5v (Scythe Ultra Kaze)
Ultra Kaze 3000 (Scythe Ultra Kaze)
Ultra Kaze 3000 @5v (Scythe Ultra Kaze)
Ultra Kaze 3000 x 2 (Scythe Ultra Kaze)
UltraK-3000 x 2 @5v (Scythe Ultra Kaze)
X-Silent 140 (Thermalright)
YL D12SH @5v (Yate Loon)
YL D12SH x 2 @5v (Yate Loon)
YL D12SH-12 (Yate Loon)
YL D12SH-12 x 2 (Yate Loon)
YL D12SL-12 (Yate Loon)
YL D12SL-12 LED (Yate Loon)
YL D12SL-12 x 2 (Yate Loon)
YL D14SH-12 (Yate Loon)
YL D14SM-12 (Yate Loon)
ZM-F3 (Zalman)
ZM-F3 x 2 (Zalman)
Fan performance, arranged by temperatures over ambient
Fan performance, arranged by Sound Pressure Level (SPL)
Single and Double fan setups, all at 12v, by temp over ambient.
Single and double fan setups, 12v, arranged by SPL
Single 120mm fan setups, by temp over ambient
Double 120mm fan setups, by temp over ambient
Temps over ambient vs RPM's.
Spreadsheet with data:
https://spreadsheets.google.com/ccc?...reFNjSXc&hl=en
ehume is offline
post #3 of 411 (permalink) Old 05-02-2010, 03:55 PM - Thread Starter
Retired Reviewer
ehume's Avatar
What do you do when you want to run your Intel i7 860 at 4GHz with air cooling? My approach was to get a Prolimatech Megahalems. I bought some Noctua low noise fans. I’m set, right? I can run my computer in my non-airconditioned computer room and use it all summer, right?
Wrong. It turns out that I had bitten off a bit of a challenge. I was going to need some stronger fans. But to choose fans I couldn’t just rely on fan specs. Many companies selling items to consumers present specifications that are not always accurate (I’m being charitable here). I couldn’t just read reviews, since they were either oriented to radiators (the Megahalems is not a radiator) or to case fan use, or used methodology that was not helpful to me. Besides, how do airflow (in CFM) or static pressure relate to the cooling power of a Megahalems? I could just buy a real brute of a fan, but the computer must sit on my desk not far from my ears. I wanted a balance between performance and noise.
I decided to test a lot of fans to see what they could do to cool my system down. Since the Megahalems is designed not to put up much resistance to airflow, I decided that I would also use it as a proxy for testing the airflow of various fans so I could determine which fans I would prefer as case fans. So I tested a number of fans that ranged in CFM. In the end, I tested 65 fans in 112 configurations. I tested them in forty-minute runs, sometimes more than once.
Limits
I don’t want to cook my chip. Yes, I know they can handle lots of heat, but I decided I would stay within official parameters. That meant, for example, that I don’t want to let the temp at the center of the heatspreader – Intel’s official measuring point – exceed the “thermal design power” of the chip, which is 72.7c. Now, I do get a reading from my motherboard that seems to be the heatspreader temp (HST). The motherboard software calls it the “system temperature.” But I am not absolutely sure that the system temperature is the HST. In any case, my hottest cpu core temp consistently runs 9c over the system temp. Also, because the cpu temps are higher they are more accurate because the chip reports not the actual temperature but the distance in centigrade from the maximum allowed junction temperature – the chip will throttle itself above its Tjmax of 99-100c – and the smaller the distance from the reported temp to Tjmax, the more accurate it is. Finally, when people report temps they report cpu core temps. So I will report cpu temps, and the max cpu temp I will allow is 80c. I could push that to 81.7c but I don’t trust the accuracy of the sensors. I am also concerned about heat transfer.
Working backwards, then, the max allowable difference in temperature over ambient will be 50c. This gives me a rough measure that I can transfer from my basement workshop where the ambient is 16-19c to our computer room where the ambient can reach 30c. I call it a rough measure because the higher the ambient, the less the capacity of a heat source to transfer heat to a heatsink. Because I do not know what the magnitude of this difference is, I am keeping a max heat difference of 50c and not 51.7c.
The Setting and the Setup
My Basement workshop is cool and quiet, with ambient temps ranging from 16c to 19c, and ambient noise less than 10 dBA when there is no activity upstairs.
The chip and motherboard are set in an NZXT Beta Evo that has had its top and back grills removed, and set on its side. The Megahlems was oriented front to back (or right to left, if you will). The exhaust from the heatsink blew right out the back where the rear grill used to be. The case was not moved for the duration of the testing, and the side panel was left off. No case fans operated during the testing.
TIM was Gelid Solutions GC Extreme (GC-3) applied as a double grain of rice in the center of the heatsink. The video card is a low performance ( = cheap) fanless card.
The fans were connected to the motherboard CPU fan header using a fan Y-type cable splitter. The yellow RPM reporter wire on the exhaust fan was split off from the Y-cable and connected to another fan header on the motherboard so that RPM’s from each fan could be monitored. However, with 5-volt testing I rigged a pair of Molex adapters to provide 5v power to the fans while allowing RPM monitoring.
The reason for connecting the fans to the motherboard cpu fan header is that during normal use each heatsink fan (HSF) will be on Auto – controlled by the motherboard to respond to cpu temps. During idle there is no need for a fan to be going flat out.
Speaking of not going flat out, you may well ask why I tested fans at 5 volts. I was trying to get some idea of how loud these fans would be, and how well they would perform undervolted. Why not use a fan controller? Some fan controllers make fans sound bad when they are undervolted. So I simply used the 5v line from Molex to test fans at the lower voltage. This way we get an honest result, untainted by a less than stellar controller.
The Overclock
The i7 860 I am using has reached a BCLK of 230MHz on 1.396v. This was with the motherboard on Auto. The max for the chip is 1.4v. The motherboard has been reliable: it has never let the voltage go over 1.396v on Auto. This chip has also gone to 4.5GHz at BCLK 207MHz. But I did not and do not have cooling systems to allow me to stress test my system at those speeds and voltages.
For a 4GHz overclock, the user of an i7 860 has a few choices: a 200MHz BCLK with a 20x multiplier (= 4000MHz), 191 x 21 = 4011MHz, and 182 x 22 = 4004MHz. Higher BCLK’s require higher voltages, so the 182MHz BCLK was the obvious choice. Unfortunately, the chip won’t allow higher multipliers so a lower BCLK cannot be used.
The motherboard sets voltages in increments. The lowest setting that would allow a twelve hour run of LinPack was 1.31250v. With Load Line Calibration enabled, the cores get up to 1.328v under max load. Vtt is 1.19v (absolute max allowed is 1.21v). Vdimm is set to 1.620v and runs at 1.616v. Oh, yes: hyperthreading is enabled.
As for stability: on top of the twelve hour OC stability runs, the rig has done at least 150 forty-minute fan test runs of OCCT/LinPack with exactly zero errors.
The Instruments
For ambient temps I have a digital thermometer. It measures in Fahrenheit, so I convert to centigrade and round to the nearest 0.5c. The basement is not only cool, but the ambient temp changes slowly. For cpu temps I use Real Temp to record max temps, and OCCT to graph the cpu temps. Both rely on what the motherboard (a Gigabyte GA-P55A-UD3P) reports from the cpu sensors.
For RPM’s I use EasyTune6, the app Gigabyte bundles with its motherboards. The RPM jumps around. Even on Speedfan that RPM number jumps around on all of these fans. So I try to assess the average speed during peak load. The RPM readings are the least accurate aspect of these tests.
Fan sound level was measured with the Tenma 72-942 sound pressure level (SPL) meter, which purports to be accurate to 0.5 dB at 30 dB and above. It will measure quieter sounds but does not promise such accuracy. So, for example, I was able to determine that my basement has an SPL of less than 10 dBA when all is quiet upstairs, but not a definite number. For the fan SPL I measured dBA at 10cm, then converted the reading to the equivalent of 1m by subtracting 20 dB. The check on this is that certain industrial fans like San Aces give accurate specifications. The SPL meter readings were either at or close to industrial specs in free air.
I expected that the fans would all be louder on the heatsink. Fans get louder when their output is obstructed and the air pressure rises. But with the Megahalems the fans frequently were not as loud as their specs. Sometimes this was due to lower RPM’s than spec, but other times – who knows?
Fan noise is not the same as SPL, though. The Magma and the Slip Stream, for example, put out a lot more sound pressure level than noise. The SPL meter clearly picks up all of the white noise that we simply do not perceive. Comments here are important.
The Load
After comparing LinX, Prime95 and OCCT, I found I was running my hottest temps on OCCT’s Linpack module. If I were testing for stability of overclock I’d run both Prime95 and OCCT. But I’m looking for heat stress here. I tested runs of up to two hours, but I discovered I got no more information than I had at 40 minutes.
Limitations of the Testing
The CPU reports temps in 1c increments. While the System Temp reading tended to stay stable at one reading or another, the cpu temps tended to jiggle up and down. When this happened a lot, it was fairly clear that the real temp was somewhere between the upper and the lower temp, so I recorded it as x.5c. The ambient I recorded to the nearest 0.5c. I recorded the difference between the hottest cpu temp and the ambient temp as ‘temp over ambient.’
Most fans had a single run. With the more important fans I did more than one run. Where I have more than one of a fan I will try to run each copy of the fan. The results are averaged, but generally temp over ambient ranged about 1c or less between runs.
ehume is offline
post #4 of 411 (permalink) Old 05-02-2010, 03:56 PM - Thread Starter
Retired Reviewer
ehume's Avatar
When I started this investigation I had some notion that there would be a large spread in cooling prowess between fans. I thought that most of my fan testing would be at 3.6GHz, and that only the best fans would cool my system at 4GHz. So much for expectations.
Conclusions:
1. Once you get to 1000 RPM or so, there is only about a 12c difference in cooling performance between the various fans.
2. As a practical matter, fans seem to max out between 2000 and 2500 RPM. After that you need huge increases in CFM to get another degree of cooling.
3. Although putting on a second fan helps, the amount it helps depends on the power of the first fan: the more powerful the fan, the less benefit you get from a second fan.
4. TANSTAAFL: By and large, if you want more air through your cooler, you will have to pay for it with more noise.
5. The blade count doesn’t seem to make much difference in cooling, but the depth of the fan does.
Do these conclusions sound obvious? Well, isn’t it nice when hard data supports conventional wisdom? The reality check goes both ways.
A few comments on specific fans:
The San Ace 9G1212H101(1) remains the Prince of Fans, at least on the Megahalems. One of these gives the best balance between sound pressure level and cooling performance.
And the Princesses of Fans: A pair of Yate Loon D12SH-12’s gives nearly the same cooling power with slightly less noise; but at the low voltages seen at idle, they will be quieter. Also, at US$7.40 for a pair, they are far cheaper than the $18.40 a US vendor wants for a single San Ace with bare wires.
Other worthy fans: CM Blade Master, Scythe Slipstream 1600’s, and the Japan Servo “square round†fan.
Some of the fans seem to have a higher SPL than perceived noise. Slip Streams do that, for example. So do Magmas. I would be very interested in seeing what a pair of Magmas can do.
So, what’s next? Do I test these fans at 3.6GHz on the same rig? Or do I mount a Noctua NH-D14 and see what 140mm fans can do in a cooler designed for them?
In the meantime, below are a number of posts arranged by brand that have more details on the fans, their specs and their performance, along with pics.
P.S. --
Here is what the TIM spread looked like. It was Gelid Solutions GC3 Extreme:
GC3 on the heatspreader. Fan direction was right to left (east > west).
Close up of GC3 on heatspreader. And no, I have no explanation for the dark lines in the middle. When the heatspreader is cleaned with Arcticlean 1 & 2, it doesn't show up.
GC3 on the heatsink. Sorry about the lack of focus.
You experts can tell me whether I had a good mount for an unlapped set of heatspreader and heatsink.
Bonus
How to mount fan clips on a Megahalems
Start with a Megahalems:
Now, snag the lower screw hole with one end of the clip. Then draw the clip back until the shaft of the clip catches behind the corner of the fan clip groove:
A closeup of the catch:
Now pull the shaft up until it sits in the fan clip groove, then bring the end over to click into the top screw hole:
Done:
ehume is offline
post #5 of 411 (permalink) Old 05-02-2010, 03:56 PM - Thread Starter
Retired Reviewer
ehume's Avatar
Akasa
Akasa Apache
Image: Akasa Apache, exhaust view
Image: Akasa Apache, intake view
I got an Akasa Apache because I like to read about airplanes and Akasa’s pictures of this fan – taken from the side – made the blades look like the blades of a large jet engine compressor. Neat! I thought.
Link: http://www.akasa.com.tw/update.php?t...model=AK-FN057
Akasa Apache Specs:
Size: 120x25mm, 9 blades
Bearing: HDB (Hydro Dynamic Bearing)
Speed: 600 – 1300 RPM, PWM control
Airflow: up to 57.53 CFM
SPL: 6.9 -16.05 dB(A)
Features: IP-54 military standard moisture and dust protection. PWM control
Results on the Megahalems:
Speed: 1415 rpm
CPU temp over ambient: 58.5c
SPL: 26 dBA
In my opinion this fan would do better as a case fan than a HSF. More recently Akasa has released a PWM fan with an RPM spread better suited to overclocking. The Viper fan ranges from 600 to 1900 RPM. If you’re thinking of getting an Apache for a HSF, I’d recommend a Viper instead.
Link: http://www.akasa.com.tw/update.php?t...model=AK-FN059
ehume is offline
post #6 of 411 (permalink) Old 05-02-2010, 03:57 PM - Thread Starter
Retired Reviewer
ehume's Avatar
Antec
Antec Tri-Cool
This fan came with my case. It comes with a Molex connector for power and has a three-way switch for speed control. It does not have an RPM reporting lead, so speeds must be estimated. I synchronized another fan with it, then read the RPM of that fan.
Image: Antec Tri-Cool exhaust view
Image: Antec Tri-Cool intake view
Link: http://www.antec.com/pdf/manuals/NSK..._EN_Manual.pdf (a PDF; see page 7 for fan specs)
Antec Tri-Cool Specs:
Size: 120x25mm, 7 blades
Bearing: not specified
Feature: 3-way speed switch
Antec Tri-Cool High setting:
Specs:
Speed: 2000 RPM
Airflow: 79 CFM
SPL: 30 dBA
Speed: 1930 RPM (estimated by synchronizing with another fan)
CPU temp over ambient: 54.5c
SPL: 32 dBA
Antec Tri-Cool Medium setting:
Specs:
Speed: 1600 RPM
Airflow: 56 CFM
SPL: 28 dBA
Speed: 1560 RPM (estimated by synchronizing with another fan)
CPU temp over ambient: 56c
SPL: 27 dBA
Antec Tri-Cool Low setting:
Specs:
Speed: 1200 RPM
Airflow: 39 CFM
SPL: 25 dB(A)
Speed: 1050 RPM (estimated by synchronizing with another fan)
CPU temp over ambient: fail
SPL: 17.5 dBA
ehume is offline
post #7 of 411 (permalink) Old 05-02-2010, 03:57 PM - Thread Starter
Retired Reviewer
ehume's Avatar
Arctic Cooling
Arctic Fan 12 L (discontinued)
I got this fan as part of a deeply discounted random collection of fans. From looking at it you’d think it is only a case fan. Yet a 92mm version of this fan is the air mover for the AC Freezer Pro 7, an excellent little CPU cooler. One unusual aspect of this fan: when you look at it from the intake side the blades rotate clockwise. Also, the exhaust is the open side of this fan.
Image: Arctic Cooling 12L, exhaust view
Image: Arctic Cooling 12L, intake view
Link: http://www.arctic-cooling.com/catalo...=146&page=spec
Arctic Cooling 12L Specs:
Size: 120x38mm, 7 blades. Essentially an open 120x25mm fan in a cage.
Bearing: fluid dynamic bearing
Speed: 1000 RPM
Airflow: 37 CFM
SPL: 20.0 dB(A)
Speed: 1030 RPM
SPL: 21 dBA
ehume is offline
post #8 of 411 (permalink) Old 05-02-2010, 03:58 PM - Thread Starter
Retired Reviewer
ehume's Avatar
Bulk
“Two Dollar Fan”
I wanted a shroud. That meant tearing the guts out of a fan. I found a fan discounted to $2US (normally $2.79). But it was too nice a fan to kill, so I kept it. When I got my grab bag (a deeply discounted random collection of fans) it contained some useless fans which are now shrouds, thus preserving this “bulk” fan.
Link: http://www.geeks.com/details.asp?invtid=12025-BULK
Image: Bulk Two Dollar Fan, exhaust view
Image: Bulk Two Dollar Fan, intake view
Look at the blade shape. It looks just like a Scythe S-Flex, or a more recent Yate-Loon. Will this fan perform well?
Specs:
Sleeve bearing
You were expecting specs?
Two Dollar Fan Results on the Megahalems:
Speed: 1500 RPM
CPU temp over ambient: 55.5c
SPL: 27.5 dBA
It did better than the Akasa Apache. It essentially matched the Enermax Magma, with less noise. YMMV.
ehume is offline
post #9 of 411 (permalink) Old 05-02-2010, 03:59 PM - Thread Starter
Retired Reviewer
ehume's Avatar
Cooler Master
R4-L2R-20AC-GP, with blue LED’s
Image: Cooler Master R4-2R 20AC-GP, exhaust view
Image: Cooler Master R4-2R 20AC-GP, intake view
Link: http://www.coolermaster-usa.com/prod...roduct_id=2915
Cooler Master R4-2R 20AC-GP Specs:
Bearing: Long Life Sleeve
Speed: 2000 RPM
Airflow: 69 CFM
SPL: 19 dB(A)
Static Pressure: 3.04 mm H2O
Features: Blue LED’s
Speed: 1750 RPM
CPU temp over ambient: 54c
SPL: 27.5dBA
CM Blade Master
I bought two. CM was offering them refurbished for $7.99 each plus shipping. Who could pass that up?
Links: http://cmstore.coolermaster-usa.com/...roducts_id=420
http://cmstore.coolermaster-usa.com/...roducts_id=380
Image: Cooler Master Blade Master 120mm fans, intake & exhaust
Image: Megahalems, Blademasters and shrouds – closeup
I like these fans. Very pleasant. Shrouds do not help them, at least on the Megahalems.
CM Blade Master Specs:
Speed: 600 - 2000 R.P.M., PWM control
Airflow: 21.2 - 76.8 CFM
SPL: 13 – 32 dBA
Static Pressure: 0.40 – 3.90 mmH2O
Features: PWM control. Comes with corner pads.
Average of two fans individually:
Speed: 1950 RPM
CPU temp over ambient: 52.5c
SPL: 33 dBA
Two fans in tandem:
Speed: 1995 RPM (average)
CPU temp over ambient: 51.5c
SPL: 36.5 dBA
ehume is offline
post #10 of 411 (permalink) Old 05-02-2010, 03:59 PM - Thread Starter
Retired Reviewer
ehume's Avatar
Coolink
SWiF2-1201
Who could pass up an eleven-bladed fan? Just to see what it can do.
Image: Coolink SWiF2-1201 exhaust view
Image: Coolink SWiF2-1201 intake view
Link: http://www.coolink-europe.com/en/categories/23_29.html
Coolink SWiF2-1201 Specs:
Size: 120x25mm, 11 blades
Bearing: hydro-dynamic bearing
Speed: 1200 RPM
Airflow: 55.44 CFM
SPL: 18.2 dBA
Static Pressure: na
Features: Anti-Vibration Bolts & Screws
Speed: 1275 RPM
CPU temp over ambient: 60c
SPL: 24.5 dBA
The 1201 would be fine as a case fan. There is a PWM version that has a speed range of 800 – 1700 RPM. This would be more suitable as a HSF.